What does Article 600 require of the disconnecting means for a sign?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 10003
- D: It must open all ungrounded conductors and be within sight of the sign or lockable in the open position
Explanation
Each sign and outline lighting system must have an externally operable disconnect that opens all ungrounded conductors. It must be within sight of the sign or, if not, capable of being locked in the open position.
More questions: Special Equipment, Pools, PV and EV
- 10004Which statement about fixed electric signs is correct?
- 10005What is required of the main disconnecting means for an elevator?
- 10009When may an information technology equipment room use the special provisions of Article 645?
- 10011Branch-circuit conductors supplying information technology equipment under Article 645 must have an ampacity of not less than what percentage of the total connected load?
- 10012What is the minimum horizontal distance from the inside wall of a permanently installed pool for a general purpose 125-volt receptacle?
- 10013125-volt, 15- and 20-ampere receptacles located within what distance of the inside walls of a pool require GFCI protection?