The disconnecting means for crane runway conductors must be of what type?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 10008
- C: Readily accessible, operable from the ground or floor, and lockable open
Explanation
A disconnecting means for runway conductors must be readily accessible and operable from the ground or floor level, open all ungrounded conductors, and be lockable open. This lets personnel de-energize the crane before working on it.