In an information technology equipment room using Article 645, where must the remote disconnect controls be located?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 10010
- B: At approved locations readily accessible to authorized personnel and emergency responders, typically principal exit doors
Explanation
Remote disconnect controls must disconnect power to all electronic equipment and the dedicated HVAC systems serving the room. They must be grouped, identified, and placed at approved locations readily accessible to authorized personnel and emergency responders.
More questions: Special Equipment, Pools, PV and EV
- 10011Branch-circuit conductors supplying information technology equipment under Article 645 must have an ampacity of not less than what percentage of the total connected load?
- 10012What is the minimum horizontal distance from the inside wall of a permanently installed pool for a general purpose 125-volt receptacle?
- 10013125-volt, 15- and 20-ampere receptacles located within what distance of the inside walls of a pool require GFCI protection?
- 10014At a dwelling with a permanently installed pool, where must the required 125-volt, 15- or 20-ampere receptacle be located?
- 10015A receptacle supplying a pool pump motor must be located at least how far from the inside walls of the pool?
- 10016Over an outdoor pool, what is the minimum height of a luminaire or ceiling fan above the maximum water level?