Switching devices must be located at least how far horizontally from the inside walls of a pool, unless separated by a solid fence, wall, or permanent barrier?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 10018
- A: 5 ft
Explanation
Switching devices must be at least 5 ft horizontally from the inside walls of a pool unless separated by a solid fence, wall, or other permanent barrier, or listed for use within 5 ft. This keeps a person standing in or at the edge of the pool from operating a switch with wet hands.
More questions: Special Equipment, Pools, PV and EV
- 10020Unless listed for a lesser depth, the top of the lens of a wet-niche luminaire must be at least how far below the normal water level?
- 10021A branch circuit supplies an underwater pool luminaire operating above the low-voltage contact limit. What protection is required?
- 10022For sinusoidal ac, the low-voltage contact limit used in Article 680 is how many volts RMS?
- 10025What is the minimum size of a solid copper equipotential bonding conductor for a permanently installed pool?
- 10027Perimeter surfaces around a pool must be bonded for what minimum horizontal distance beyond the inside walls?
- 10030For conductive pool shells, perimeter surface bonding must attach to the structural reinforcing steel or copper grid at a minimum of how many points?