A partially protected location under a canopy or a roofed open porch is classified in the NEC as a:
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 1098
- C: Damp location
Explanation
Article 100 lists partially protected locations under canopies, marquees, roofed open porches and similar areas as damp locations. Locations exposed directly to weather or saturated with water are wet locations.