Question 1105 of 749 · Maryland Journeyperson Electrician Exam
For circuits rated over 100 amperes, or conductors larger than 1 AWG, terminations are generally based on which conductor temperature column?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 1105
- D: 75 degrees C
Explanation
110.14(C)(1)(b) permits conductors for circuits over 100 A or larger than 1 AWG to be used at their 75 degree C ampacity, unless the equipment is listed for a higher temperature.
More questions: Definitions, Theory and Plans
- 1106Copper and aluminum conductors may be joined in the same terminal or splicing connector only when:
- 1108The required depth of working space in front of a 120/240-volt panelboard (150 volts or less to ground) is, for all conditions:
- 1109A 480Y/277-volt panelboard has exposed live parts on one side of the working space and a grounded concrete wall on the other (Condition 2). What is the minimum depth of working space?
- 1110Equipment at 277 volts to ground has exposed live parts on both sides of the working space (Condition 3). The minimum working space depth is:
- 1111What is the minimum width of the working space in front of electrical equipment covered by 110.26(A)?
- 1112For service equipment and panelboards, the minimum headroom of the working space is generally: