An 8-unit building has 900 ft2 units, each with two small-appliance and one laundry circuit. What is the NEC 2020/2023 standard method demand for these loads?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 12102
- B: 22,110 VA
Explanation
Each unit is 900 x 3 VA + 4,500 VA = 7,200 VA, for 57,600 VA in total. With the dwelling demand factors: 3,000 + 54,600 VA x 0.35 = 22,110 VA.