Nine 5 kW electric dryers in a multifamily building are on one service. Using the NEC 2020 or 2023 dryer demand factors, what is the dryer load?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 12117
- A: 24,750 VA
Explanation
9 x 5,000 VA = 45,000 VA. The demand factor for nine dryers is 55 % (Table 220.54), so the load is 24,750 VA.
More questions: Load Calculations
- 12118Standard method (NEC 2020/2023): the only fastened-in-place appliances are a 1,000 VA dishwasher, an 800 VA disposal and a 4,000 W water heater. What appliance load goes into the calculation?
- 12119Standard method (NEC 2020/2023): a dwelling has a 1,200 VA dishwasher, 700 VA disposal, 5,500 W water heater, 1,000 VA microwave and 600 VA attic fan, all fastened in place. What is the appliance demand load?
- 12120What is the demand load for one 10.5 kW household range under the NEC 2020 or 2023?
- 12121Using the NEC 2020 or 2023 standard method, what is the demand load for one 17 kW range?
- 12122Nine 13 kW ranges serve an apartment building. Under the NEC 2020 or 2023, what is the range demand load?
- 12021Using the standard method under the NEC 2020/2023, what general lighting load must be included in the service calculation for a one-family dwelling with 2,400 ft2 of livable floor area?