Question 13004 of 749 · Maryland Journeyperson Electrician Exam
A heater rated 4,000 watts at 240 volts is connected to a 208 volt supply. Assuming constant resistance, about how much power will it produce?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 13004
- D: 3,004 W
Explanation
Power varies with the square of voltage at constant resistance: P = 4,000 x (208 / 240) squared = about 3,004 W. Scaling only linearly by 208 / 240 gives the common wrong answer of 3,467 W.
More questions: Electrical Calculations
- 13005A current of 10 amperes flows through a conductor path with a total resistance of 0.5 ohm. How much power is lost as heat in the conductors?
- 13006A balanced three-phase 480 volt resistive load is rated 50 kW. What is the line current?
- 13007What is the full-load line current of a balanced 30 kVA three-phase load supplied at 208 volts?
- 13008A single-phase 240 volt resistive load draws 32 amperes. What is the load in kilowatts?
- 13009A three-phase 480 volt motor draws 40 amperes per line at a power factor of 0.85. What is the true power input?
- 13010A load consumes 72 kW at a power factor of 0.80. What is the apparent power?