Question 13052 of 749 · Maryland Journeyperson Electrician Exam

Six current-carrying 8 AWG THHN copper conductors are in one raceway at 30 °C ambient, and all terminations are rated 75 °C. What is the maximum ampacity that may be used for each conductor?

Exactly one answer is correct.

Show solution

Correct answer to question 13052

  • D: 44 A

Explanation

The derated value from the 90 °C column is 55 x 0.80 = 44 A, while the 75 °C termination limit is 50 A. The lower of the two governs, so 44 A may be used.

Next to question ›