What adjustment factor applies when 25 current-carrying conductors are installed in a single raceway longer than 24 inches?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 13061
- A: 45 %
Explanation
The adjustment table assigns 45 % to 21 through 30 current-carrying conductors. 50 % covers 10 to 20, 40 % covers 31 to 40, and 35 % applies to 41 and above.