Question 13112 of 749 · Maryland Journeyperson Electrician Exam

What is the maximum continuous load permitted on a 20 A branch circuit protected by a standard (not 100 % rated) breaker?

Exactly one answer is correct.

Show solution

Correct answer to question 13112

  • D: 16 A

Explanation

A continuous load may not exceed 80 % of the overcurrent device rating, which is the inverse of the 125 % rule: 20 x 0.80 = 16 A. Loading the circuit to the full 20 A is allowed only for noncontinuous loads.

Next to question ›