Question 2014 of 749 · Maryland Journeyperson Electrician Exam
What is the minimum size copper conductor permitted for an overhead service drop, other than for limited loads?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 2014
- D: 8 AWG
Explanation
Overhead service conductors must not be smaller than 8 AWG copper or 6 AWG aluminum or copper-clad aluminum. Smaller conductors down to 12 AWG hard-drawn copper are allowed only for limited loads of a single branch circuit. See 230.23(B).
More questions: Services and Service Equipment
- 2016Where must a service head generally be located in relation to the point of attachment of the service drop?
- 2017What is the minimum width of the working space in front of service equipment?
- 2018Which of the following may not be used to support overhead conductor spans?
- 2019Which types of surge protective device satisfy the dwelling unit service surge protection rule?
- 2020Service-entrance cable run on the outside of a building must be supported within 12 in. of the service head and at intervals not exceeding what distance?
- 2021A commercial service supplies 120 A of continuous load and 40 A of noncontinuous load. What is the minimum ampacity of the service-entrance conductors?