Question 2062 of 749 · Maryland Journeyperson Electrician Exam

May branch circuit conductors be installed in the same raceway as service-entrance conductors?

Exactly one answer is correct.

Show solution

Correct answer to question 2062

  • B: No, only service conductors and grounding or bonding conductors may share it

Explanation

Conductors other than service conductors may not be installed in the same service raceway or service cable. Grounding electrode conductors and supply-side bonding jumpers are an exception. See 230.7.