May branch circuit conductors be installed in the same raceway as service-entrance conductors?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 2062
- B: No, only service conductors and grounding or bonding conductors may share it
Explanation
Conductors other than service conductors may not be installed in the same service raceway or service cable. Grounding electrode conductors and supply-side bonding jumpers are an exception. See 230.7.