Question 3002 of 749 · Maryland Journeyperson Electrician Exam
When the handle of a circuit breaker is operated vertically, what position must be the on position?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 3002
- D: Up
Explanation
Where breaker handles are operated vertically, the up position must be the on position. See 240.81.
More questions: Feeders and Overcurrent Protection
- 3004A series combination rating may not be used when motors connected between the two devices contribute more than what percentage of the lower-rated breaker's interrupting rating?
- 3005When may a feeder OCPD be sized at 100 percent of the continuous load?
- 3006In which case is the next size up rule not permitted?
- 3007The available fault current at a panelboard is 18,000 A. Which breaker interrupting rating is acceptable?
- 3008What is the maximum rating of a plug fuse?
- 3009A feeder is protected at 400 A. What is the minimum copper THWN tap conductor at 75 degrees C for a 25 ft tap?