Question 4018 of 749 · Maryland Journeyperson Electrician Exam
A 125-volt receptacle is installed on the roof of an office building for servicing a rooftop unit. What protection is required?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 4018
- A: GFCI protection
Explanation
Rooftops are a listed location in 210.8(B) for other than dwelling units, so the receptacle needs GFCI protection. The servicing receptacle required near HVAC equipment by 210.63 is commonly in this location.
More questions: Branch Circuits, GFCI and AFCI
- 4019In a fitness center, which of the following areas requires GFCI protection for its 125-volt receptacles under 210.8(B)?
- 4022In a commercial building, which of the following areas is excluded from the garage and service bay GFCI requirement in 210.8(B)?
- 4023A receptacle in a commercial building is located in an unfinished basement area used for storage. Is GFCI protection required?
- 4024A 125-volt receptacle in an office break room is 4 ft from the break room sink. Is GFCI protection required?
- 4030Under the NEC 2020 and 2023, dwelling unit outdoor outlets on single-phase branch circuits rated 150 volts or less to ground require GFCI protection up to what branch circuit rating?
- 4038In a dwelling unit, which of the following locations requires AFCI protection for 120-volt, 15- and 20-ampere branch circuits supplying outlets?