Question 4051 of 749 · Maryland Journeyperson Electrician Exam
How may the receptacle outlet for a dwelling kitchen refrigerator be supplied?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 4051
- A: From a small-appliance circuit or an individual 15 A or larger circuit
Explanation
210.52(B)(1) Exception No. 2 permits the refrigerator receptacle to be supplied by an individual branch circuit rated 15 amperes or greater instead of a small-appliance circuit. It may also simply be on one of the small-appliance circuits.