Question 4076 of 749 · Maryland Journeyperson Electrician Exam
A receptacle in a dwelling living room is installed 6 ft above the floor. Does it count toward the required wall space receptacles?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 4076
- D: No, receptacles more than 5 1/2 ft above the floor do not count
Explanation
210.52 states that receptacles located more than 5 1/2 ft above the floor are not counted as required receptacle outlets. They are permitted but additional receptacles are needed lower on the wall.
More questions: Branch Circuits, GFCI and AFCI
- 4077A floor receptacle in a dwelling family room may count as the required receptacle for a wall space if it is located within what distance of the wall?
- 4078How many receptacle outlets in a hotel guest room must be readily accessible when the remaining receptacles are located for convenient furniture placement?
- 4079A hotel guest suite includes permanent provisions for cooking. Which receptacle rules apply to the suite?
- 4080A 20-ampere branch circuit supplies two or more receptacles. Which receptacle ratings are permitted?
- 4081A single receptacle is installed on an individual 20-ampere branch circuit. What is the minimum rating of the receptacle?
- 4082What is the maximum cord-and-plug load permitted on a 20-ampere receptacle supplied by a 20-ampere branch circuit with multiple outlets?