A branch circuit supplies 24 amperes of continuous load and 6 amperes of noncontinuous load. What is the minimum standard overcurrent device rating?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 4089
- A: 40 amperes
Explanation
210.20(A) requires the overcurrent device to be at least 125 percent of the continuous load plus the noncontinuous load: 24 A x 1.25 = 30 A, plus 6 A = 36 A. The next standard size at or above 36 A in 240.6 is 40 A.