Question 4101 of 749 · Maryland Journeyperson Electrician Exam
A dwelling attic contains a furnace that requires servicing. What lighting outlet is required?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 4101
- D: A lighting outlet at or near the equipment, switched at the point of entry
Explanation
210.70(A)(3) requires at least one lighting outlet with a switch or listed control at the point of entrance in attics, underfloor spaces and similar areas containing equipment that requires servicing. The lighting outlet must be at or near the equipment.
More questions: Branch Circuits, GFCI and AFCI
- 4102For a dwelling, which of the following is NOT considered an outdoor entrance for the required exterior lighting outlet?
- 4103A 12 AWG copper THHN conductor has a 90 C ampacity of 30 amperes in Table 310.16. What is the maximum overcurrent protection generally permitted for it?
- 4104What is the ampacity of a 6 AWG copper THWN conductor in the 75 C column of Table 310.16?
- 4105A 30-ampere branch circuit terminates on equipment whose terminals are not marked with a temperature rating. Which column of Table 310.16 must be used to select the conductor?
- 4106An 8 AWG copper THHN conductor connects to terminals rated 75 C on both ends. What ampacity may be used for the circuit?
- 4107For a circuit rated over 100 amperes with conductors larger than 1 AWG, which temperature column may be used for termination purposes unless equipment is marked otherwise?