Question 4108 of 749 · Maryland Journeyperson Electrician Exam

When 90 C rated THHN conductors are installed with 75 C terminations, what is the 90 C ampacity used for?

Exactly one answer is correct.

Show solution

Correct answer to question 4108

  • D: As the starting value for adjustment and correction factors

Explanation

110.14(C) allows conductors with higher temperature ratings to use their higher ampacity for ampacity adjustment, correction or both. The final result may not exceed the ampacity at the termination temperature.

Next to question ›