Question 5011 of 749 · Maryland Journeyperson Electrician Exam
A single rod electrode does not need a supplemental electrode only if its resistance to earth is
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 5011
- C: 25 ohms or less
Explanation
A single rod, pipe, or plate electrode must be supplemented by an additional electrode unless it has a resistance to earth of 25 ohms or less. See 250.53.
More questions: Grounding and Bonding
- 5012Where two ground rods are installed to meet the supplemental electrode requirement, they must be spaced at least how far apart?
- 5013A ground rod measured 40 ohms, so a second rod was driven 6 ft away. The pair still measures 30 ohms. What else is required?
- 5014Which of the following is NOT permitted to be used as a grounding electrode?
- 5015The portion of a grounding electrode conductor that is the sole connection to one or more ground rods is not required to be larger than
- 5016The portion of a GEC that is the sole connection to a concrete-encased electrode is not required to be larger than
- 5017The portion of a GEC that is the sole connection to a ground ring is not required to be larger than