Question 5063 of 749 · Maryland Journeyperson Electrician Exam
A supply-side bonding jumper on the line side of the service disconnect is sized from
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 5063
- C: Table 250.102(C)(1) based on the ungrounded service conductors
Explanation
Supply-side bonding jumpers are sized from Table 250.102(C)(1) using the largest ungrounded conductors within the raceway or enclosure. No OCPD protects these conductors, so Table 250.122 does not apply. See 250.102(C).
More questions: Grounding and Bonding
- 5064In NEC 2020 and NEC 2023, grounding requirements specific to systems over 1000 V are located in
- 5001At a building or structure, which of the permitted grounding electrodes must be bonded together to form the grounding electrode system?
- 5002A metal underground water pipe qualifies as a grounding electrode only if it is in direct contact with the earth for at least what length?
- 5003When a metal underground water pipe is used as a grounding electrode, what else does the Code require?
- 5004Under the general rule, interior metal water piping located more than what distance from its point of entrance may NOT be used to interconnect electrodes that are part of the grounding electrode system?
- 5005A concrete-encased electrode made of bare copper conductor must be at least 20 ft long and not smaller than what size?