What is the minimum cover for direct burial cable installed under a 4 in thick concrete slab with no vehicular traffic that extends at least 6 in beyond the installation?

Exactly one answer is correct.

Show solution

Correct answer to question 6005

  • A: 18 in

Explanation

Under a minimum 4 in exterior concrete slab with no vehicular traffic, extending at least 6 in beyond the installation, direct burial cable needs 18 in of cover and raceways need 4 in. See Table 300.5 in NEC 2020 and 2023; the underground installation rules are in 300.7 in NEC 2026.