What is the minimum cover for direct burial cable installed under a 4 in thick concrete slab with no vehicular traffic that extends at least 6 in beyond the installation?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 6005
- A: 18 in
Explanation
Under a minimum 4 in exterior concrete slab with no vehicular traffic, extending at least 6 in beyond the installation, direct burial cable needs 18 in of cover and raceways need 4 in. See Table 300.5 in NEC 2020 and 2023; the underground installation rules are in 300.7 in NEC 2026.