Question 6026 of 938 · Maryland Journeyperson Electrician Exam
NM cable enters a single-gang nonmetallic box that has no cable clamps. Within what distance of the box must the cable be secured?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 6026
- B: 8 in
Explanation
For single-gang nonmetallic boxes not larger than 2 1/4 in by 4 in mounted in walls or ceilings, clamps are not required if the cable is fastened within 8 in of the box and the sheath extends at least 1/4 in inside. See 314.17.
More questions: Wiring Methods, Conductors and Boxes
- 6027Type MC cable must generally be secured within 12 in of each box and at intervals not exceeding
- 6028Type AC cable must be secured within 12 in of each box and at intervals not exceeding
- 6029In an accessible suspended ceiling, an unsupported length of MC cable from the last support to a luminaire is permitted up to
- 6030How may branch circuit wiring above a fire-rated floor-ceiling assembly be supported?
- 6031May a raceway be used as the means of support for other cables, such as thermostat wiring, under the general rule?
- 6033In NEC 2020 and 2023, what is the maximum total of bends permitted in a run of EMT between pull points?