A conduit nipple not exceeding 24 in long between boxes may be filled to what percent of its area?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 6038
- B: 60 percent
Explanation
Nipples 24 in or shorter may be filled to 60 percent of their total cross-sectional area, and the adjustment factors for more than three current-carrying conductors do not apply to them. See Chapter 9 notes to tables.