Question 7012 of 871 · Maryland Journeyperson Electrician Exam
May a receptacle be installed face up in a kitchen countertop?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 7012
- B: Only if the receptacle assembly is listed for countertop or work surface use
Explanation
Section 406.5(G)(1) (406.14 in NEC 2026) prohibits receptacles installed face up in countertops or similar work surfaces unless the receptacle assembly is listed for that application. Spilled liquids can otherwise enter the contacts. Pop-up assemblies listed for countertops are the usual solution.
More questions: Equipment, Devices and Luminaires
- 7013What is the rule for installing a receptacle near a bathtub or shower?
- 7014How is an isolated ground receptacle identified on its face?
- 7015In a new dwelling, a switch box for a bedroom lighting switch is fed with cable. What does the code generally require in that box?
- 7016Which condition allows a lighting switch box to be installed without a grounded conductor under 404.2(C)?
- 7017When may a switch disconnect the grounded conductor of a circuit?
- 7018Three-way and four-way switches must be wired so that switching is done in which conductor?