A plug-in circuit breaker is back-fed to supply a panelboard. How must it be installed?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 7033
- A: Secured by an additional fastener that requires more than a pull to release it
Explanation
Section 408.36(D) requires back-fed plug-in breakers to be secured in place by an additional fastener that requires other than a pull to release. Otherwise a breaker with energized line terminals could be pulled off the bus.