Question 7049 of 749 · Maryland Journeyperson Electrician Exam

A 4500 watt, 240 volt storage water heater is installed. What minimum ampacity must the branch circuit provide?

Exactly one answer is correct.

Show solution

Correct answer to question 7049

  • C: 23.4 A

Explanation

The heater draws 4500 W divided by 240 V, which is 18.75 A. Section 422.13 requires 125 percent, so 18.75 A times 1.25 gives 23.4 A. A 25 or 30 ampere circuit with suitable conductors meets this.

Next to question ›