What does the dedicated electrical space above a panelboard extend to?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 7067
- A: 6 ft above the equipment or the structural ceiling, whichever is lower
Explanation
Section 110.26(E)(1)(a) reserves the space equal to the width and depth of the equipment, extending from the floor to 6 ft above the equipment or to the structural ceiling, whichever is lower. No piping, ducts or foreign equipment may be installed there.