Question 8038 of 749 · Maryland Journeyperson Electrician Exam
When may several motors be connected to a single branch circuit?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 8038
- B: When the conditions of 430.53 are met, such as small motors on a 120 volt 20 ampere circuit
Explanation
Section 430.53 permits two or more motors on one branch circuit under specific conditions. These include motors of 1 hp or less on circuits of 120 volts or less protected at 20 amperes or less, and other arrangements with proper overload and short-circuit protection.
More questions: Motors, HVAC, Generators and Transformers
- 8039Which nameplate value is used to size branch-circuit conductors for a packaged air conditioning unit?
- 8040An air conditioning unit nameplate shows a maximum overcurrent protection (MOCP) of 40 A. What breaker is permitted?
- 8041Where must the disconnecting means for an outdoor air conditioning condenser be located?
- 8043A rooftop HVAC unit requires a service receptacle. What is the maximum distance from the equipment?
- 8044What other location rule applies to the HVAC service receptacle?
- 8045May the HVAC service receptacle be connected to the load side of the equipment disconnecting means?