Branch-circuit conductors for a single hermetic motor-compressor must have an ampacity of at least what?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 8046
- A: 125 percent of rated-load or branch-circuit selection current, whichever is greater
Explanation
Section 440.32 requires conductors supplying a single motor-compressor to be at least 125 percent of the rated-load current or the branch-circuit selection current, whichever is greater.