A small control transformer has a primary current of 5 A and primary protection only. What is the maximum primary overcurrent device rating?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 8062
- A: 167 percent of rated primary current
Explanation
Table 450.3(B) allows 167 percent for primary currents less than 9 A but 2 A or more, when only primary protection is provided. Small transformers have relatively high magnetizing inrush.