In an RV park, what minimum percentage of the sites with electrical supply must each have a 30-ampere, 125-volt receptacle?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 9048
- A: 70 percent
Explanation
At least 70 percent of RV sites with electrical supply must each have a 30-ampere, 125-volt receptacle. A separate requirement sets the minimum share of sites with 50-ampere, 125/250-volt receptacles.
More questions: Special Occupancies
- 9049In an RV park, what minimum percentage of the sites with electrical supply must each have a 50-ampere, 125/250-volt receptacle?
- 9051At a marina, receptacles that provide shore power to boats must have individual ground-fault protection not exceeding what level?
- 9052At a marina, feeder and branch-circuit conductors installed on docks must have ground-fault protection set to open at not more than what level?
- 9053At a marina, 125-volt, single-phase, 15- and 20-ampere receptacles that do not provide shore power require what protection?
- 9055On a floating pier, electrical connections must be located at least how far above the deck?
- 9056At a marina, the disconnecting means for a shore power connection must be located within what distance of the receptacle it controls?