A pool pump motor is connected to a single-phase, 240-volt, 20-ampere branch circuit. What protection is required for the outlet?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 10042
- A: GFCI protection
Explanation
Outlets serving pool pump motors on single-phase branch circuits of 120 through 240 volts require GFCI protection whether connected by cord and plug or hardwired. NEC 2026 points to the ground-fault rules of 680.5 for the details.