Question 10044 of 749 · Maryland Journeyperson Electrician Exam
What is the maximum PV system voltage permitted for PV systems on one- and two-family dwellings?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 10044
- B: 600 volts
Explanation
On one- and two-family dwellings, the maximum PV system dc circuit voltage is 600 volts. Other buildings may go up to 1000 volts, and ground-mounted systems not on buildings may be higher.
More questions: Special Equipment, Pools, PV and EV
- 10045What is the maximum PV system voltage on or in buildings other than one- and two-family dwellings?
- 10046A PV module has a short-circuit current (Isc) of 10 amperes. Using the standard method, what is the maximum circuit current for that PV circuit?
- 10047A single PV string has modules with an Isc of 10 amperes. What is the minimum conductor ampacity before adjustment and correction, applying both 125 percent factors?
- 10049Under PV rapid shutdown rules, conductors outside the array boundary must be reduced to no more than what voltage within 30 seconds of initiation?
- 10050For PV rapid shutdown, the array boundary is defined as what distance from the array in all directions?
- 10052For one- and two-family dwellings, where must the PV rapid shutdown initiation device be located?