Inside the array boundary, one rapid shutdown option limits controlled conductors to not more than what voltage within 30 seconds of initiation?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 10051
- A: 80 volts
Explanation
Inside the array boundary, controlled conductors may be limited to 80 volts or less within 30 seconds, or a listed PV hazard control system may be used. Outside the boundary the limit is 30 volts.
More questions: Special Equipment, Pools, PV and EV
- 10052For one- and two-family dwellings, where must the PV rapid shutdown initiation device be located?
- 10053A PV system has dc circuits operating at 80 volts or more between any two conductors. What protection is required?
- 10055A PV module has an open-circuit voltage (Voc) of 40 volts. Ten modules are connected in series, and the temperature correction factor for the lowest expected ambient temperature is 1.12. What is the maximum PV circuit voltage?
- 10056A PV module has a temperature-corrected Voc of 48 volts. What is the maximum number of modules that can be connected in series on a one- and two-family dwelling?
- 10057Under the 120 percent rule for a load-side PV connection at the opposite end of the busbar, a panelboard has a 200-ampere busbar and a 200-ampere main breaker. What is the largest permitted backfed PV breaker?
- 10058A panelboard has a 225-ampere busbar and a 200-ampere main breaker. Using the 120 percent rule with the PV breaker at the opposite end, what is the largest permitted backfed PV breaker?