Question 10057 of 871 · Maryland Journeyperson Electrician Exam

Under the 120 percent rule for a load-side PV connection at the opposite end of the busbar, a panelboard has a 200-ampere busbar and a 200-ampere main breaker. What is the largest permitted backfed PV breaker?

Exactly one answer is correct.

Show solution

Correct answer to question 10057

  • B: 40 amperes

Explanation

The sum of 125 percent of the inverter output current and the main OCPD rating may not exceed 120 percent of the busbar rating: 200 A x 1.2 = 240 A, and 240 A minus 200 A leaves 40 A for the PV breaker. Placing the PV breaker at the far end of the busbar is a condition for this method.

Next to question ›