Question 10061 of 871 · Maryland Journeyperson Electrician Exam
A PV interconnection made between the service meter and the service disconnecting means is what type of connection?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 10061
- C: A supply-side connection
Explanation
Connecting a power production source on the supply side of the service disconnecting means is a supply-side connection. Load-side connections are made at or downstream of the service disconnect and are subject to the busbar limits.
More questions: Special Equipment, Pools, PV and EV
- 10062For a stationary energy storage system at a one- or two-family dwelling, where must the disconnecting means or its remote control be located?
- 10063Article 706 applies to permanently installed energy storage systems with a capacity greater than what amount?
- 10064What protection is required for receptacles installed for the connection of EV charging equipment?
- 10065An EVSE has a maximum load of 48 amperes. What is the minimum OCPD rating for the branch circuit supplying it?
- 10066An EVSE is rated 40 amperes continuous. What is the minimum OCPD rating for its branch circuit?
- 10067How must each outlet installed for EVSE be supplied?