An EVSE is rated 40 amperes continuous. What is the minimum OCPD rating for its branch circuit?

Exactly one answer is correct.

Show solution

Correct answer to question 10066

  • B: 50 amperes

Explanation

The branch-circuit OCPD must be at least 125 percent of the maximum load: 40 A x 1.25 = 50 A. 50 A is a standard OCPD size.