Question 10069 of 749 · Maryland Journeyperson Electrician Exam
In NEC 2020 and 2023, EVSE rated more than 60 amperes or more than 150 volts to ground requires a disconnecting means with which characteristics?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 10069
- D: Readily accessible and lockable open
Explanation
EVSE rated more than 60 amperes or more than 150 volts to ground must have a readily accessible disconnecting means that is lockable open. If remote, a plaque on the equipment must show its location.
More questions: Special Equipment, Pools, PV and EV
- 10076The OCPD for a fire pump motor must be sized to carry what current indefinitely?
- 10077In NEC 2020 and 2023, fire pump supply conductors inside a building may be protected by encasement in at least how much concrete?
- 10083A transformer arc welder has a rated primary current of 50 amperes and a 50 percent duty cycle. The I1eff value is not marked. Using a duty cycle multiplier of 0.71, what is the minimum supply conductor ampacity?
- 10084The OCPD for an arc welder may be rated at not more than what percentage of the rated primary current (I1max)?
- 10001Each commercial building and occupancy accessible to pedestrians must have at least one outlet for sign or outline lighting at each tenant entrance. What branch circuit must supply it?
- 10003What does Article 600 require of the disconnecting means for a sign?