During motor starting, the voltage at the fire pump controller line terminals must not drop more than what percentage below the controller rated voltage?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 10080
- B: 15 percent
Explanation
The voltage at the fire pump controller line terminals must not drop more than 15 percent below rated voltage during motor starting. During running at 115 percent of FLC, the drop must not exceed 5 percent at the motor.