A fire pump motor has a full-load current of 40 amperes and no accessory loads. What is the minimum ampacity of the supply conductors?

Exactly one answer is correct.

Show solution

Correct answer to question 10081

  • A: 50 amperes

Explanation

Fire pump supply conductors must have an ampacity of not less than 125 percent of the motor FLC plus 100 percent of accessory loads: 40 A x 1.25 = 50 A. The OCPD is sized separately, based on locked-rotor current.