Question 1089 of 749 · Maryland Journeyperson Electrician Exam
Conductors running from the service equipment to a subpanel that contains the final branch-circuit breakers are classified as:
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 1089
- B: A feeder
Explanation
Article 100 defines a feeder as the circuit conductors between the service equipment (or a separately derived system or other power source) and the final branch-circuit overcurrent device.