Question 1093 of 749 · Maryland Journeyperson Electrician Exam
Under the NEC, operation of equipment in excess of its normal full-load rating that would cause damaging overheating if it persisted is called:
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 1093
- D: An overload
Explanation
Article 100 defines overload as operation in excess of normal full-load rating, or of a conductor in excess of its ampacity, that causes damage or overheating if it lasts long enough. A short circuit or ground fault is not an overload.
More questions: Definitions, Theory and Plans
- 1094Under the NEC, a disconnect is considered in sight from the equipment it serves when it is visible and not more than:
- 1095A branch circuit with two or more ungrounded conductors having a voltage between them and a grounded conductor with equal voltage to each ungrounded conductor is a:
- 1096A building-supplied transformer whose secondary has no direct electrical connection to the supply conductors, except through grounding and bonding connections, creates:
- 1097The point of connection between the facilities of the serving utility and the premises wiring is called the:
- 1098A partially protected location under a canopy or a roofed open porch is classified in the NEC as a:
- 1099According to Article 90, the purpose of the NEC is: