How must emergency lighting systems be designed with respect to lamp failure?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 11009
- A: The failure of any individual lighting element must not leave a required space in total darkness
Explanation
Emergency lighting must be arranged so that the failure of any single lighting element, such as a lamp, will not leave in total darkness any space that requires emergency illumination. Using two or more luminaires on separate circuits, or unit equipment, meets this goal.
More questions: Emergency, Limited Energy and Communications
- 11010Where on-site emergency power sources are installed, a sign must be placed where?
- 11011Which record must be kept for an emergency system?
- 11013In assembly occupancies for more than 1000 persons or buildings above 75 ft in height, emergency feeder circuit wiring must have what protection?
- 11014In NEC 2020 and 2023, which article covers fire-resistive cable systems?
- 11016Egress lighting required by a building code to illuminate exit paths during a power outage is part of which system?
- 11017A code-required system supplies sewage disposal pumps and smoke removal equipment during outages, with less urgency than egress lighting. Which system is this?