In NEC 2020, what is the maximum OCPD for 18 AWG Class 1 circuit conductors?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 11030
- C: 7 amperes
Explanation
18 AWG Class 1 conductors must not be protected at more than 7 amperes, and 16 AWG conductors not more than 10 amperes. Larger conductors follow their ampacity.