May nonconductive optical fiber cables occupy the same raceway as electric light and power conductors operating at 1000 volts or less?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 11039
- B: Yes, they are permitted
Explanation
Nonconductive optical fiber cables may occupy the same cable tray or raceway with conductors for electric light, power, Class 1, or non-power-limited fire alarm circuits operating at 1000 volts or less. They carry no current and cannot be energized by contact.