Question 12022 of 749 · Maryland Journeyperson Electrician Exam

A 2,000 ft2 dwelling has the minimum two small-appliance circuits and one laundry circuit. Under the NEC 2020/2023 standard method, what is the demand load for general lighting, small-appliance and laundry loads combined?

Exactly one answer is correct.

Show solution

Correct answer to question 12022

  • B: 5,625 VA

Explanation

Lighting is 2,000 x 3 VA = 6,000 VA, plus 2 x 1,500 VA small-appliance and 1,500 VA laundry gives 10,500 VA (Table 220.12 in 2020, 220.41 in 2023, 220.52). Applying the dwelling demand factors (Table 220.42 in 2020, Table 220.45 in 2023): first 3,000 VA at 100 % plus 7,500 VA x 35 % = 5,625 VA.

Next to question ›