Question 12027 of 749 · Maryland Journeyperson Electrician Exam

Optional method (NEC 2020/2023): a 1,500 ft2 dwelling with two small-appliance and one laundry circuit, a 10 kW range, 5 kW dryer and 4.5 kW water heater has six separately controlled 2 kW baseboard heaters and a 4,000 VA AC unit. What is the total calculated load?

Exactly one answer is correct.

Show solution

Correct answer to question 12027

  • C: 22,200 VA

Explanation

General loads = 28,500 VA, so 10,000 VA + 40 % of 18,500 VA = 17,400 VA (220.82(B)). Four or more separately controlled heating units count at 40 %: 12,000 x 0.40 = 4,800 VA, which exceeds the 4,000 VA AC (220.82(C)). Total 22,200 VA.